发表人:luxiaojing 发表时间:2012/7/1 11:37:00  

 

 本栏论题: 西门子CPU315停机求助  [3878]

    这是诊断信息,各位大侠帮忙看一下
    Diagnostic buffer of module CPU 315-2 DP
   
    Order No./ Description Component Version
    6ES7 315-2AG10-0AB0 Hardware 1
    - - - Firmware V 2.0.0
   
    Rack: 0
    Slot: 2
   
   
    Event 1 of 100: Event ID 16# 38C4
    Distributed I/Os: station return
    Address of the affected DP slave: station number: 13
    DP master system ID: 1
    Log. base address of the DP slave: Input address: 2036
    Log. base address of the DP master: 2047
    Requested OB: Rack failure OB (OB86)
    OB not found, or disabled, or cannot be started in the current operating mode
    External error, Outgoing event
    03:06:00:727 am 06/30/12
   
   
    Event 2 of 100: Event ID 16# 38C4
    Distributed I/Os: station return
    Address of the affected DP slave: station number: 6
    DP master system ID: 1
    Log. base address of the DP slave: Input address: 2043
    Log. base address of the DP master: 2047
    Requested OB: Rack failure OB (OB86)
    OB not found, or disabled, or cannot be started in the current operating mode
    External error, Outgoing event
    03:06:00:637 am 06/30/12
   
   
    Event 3 of 100: Event ID 16# 38C4
    Distributed I/Os: station return
    Address of the affected DP slave: station number: 15
    DP master system ID: 1
    Log. base address of the DP slave: Input address: 2034
    Log. base address of the DP master: 2047
    Requested OB: Rack failure OB (OB86)
    OB not found, or disabled, or cannot be started in the current operating mode
    External error, Outgoing event
    03:06:00:547 am 06/30/12
   
   
    Event 4 of 100: Event ID 16# 38C4
    Distributed I/Os: station return
    Address of the affected DP slave: station number: 10
    DP master system ID: 1
    Log. base address of the DP slave: Input address: 2039
    Log. base address of the DP master: 2047
    Requested OB: Rack failure OB (OB86)
    OB not found, or disabled, or cannot be started in the current operating mode
    External error, Outgoing event
    03:06:00:457 am 06/30/12
   
   
    Event 5 of 100: Event ID 16# 38C4
    Distributed I/Os: station return
    Address of the affected DP slave: station number: 16
    DP master system ID: 1
    Log. base address of the DP slave: Input address: 2033
    Log. base address of the DP master: 2047
    Requested OB: Rack failure OB (OB86)
    OB not found, or disabled, or cannot be started in the current operating mode
    External error, Outgoing event
    03:06:00:367 am 06/30/12
   
   
    Event 6 of 100: Event ID 16# 38C4
    Distributed I/Os: station return
    Address of the affected DP slave: station number: 14
    DP master system ID: 1
    Log. base address of the DP slave: Input address: 2035
    Log. base address of the DP master: 2047
    Requested OB: Rack failure OB (OB86)
    OB not found, or disabled, or cannot be started in the current operating mode
    External error, Outgoing event
    03:06:00:277 am 06/30/12
   
   
    Event 7 of 100: Event ID 16# 38C4
    Distributed I/Os: station return
    Address of the affected DP slave: station number: 11
    DP master system ID: 1
    Log. base address of the DP slave: Input address: 2038
    Log. base address of the DP master: 2047
    Requested OB: Rack failure OB (OB86)
    OB not found, or disabled, or cannot be started in the current operating mode
    External error, Outgoing event
    03:06:00:196 am 06/30/12
   
   
    Event 8 of 100: Event ID 16# 3842
    Module OK
    Module type: Distributed I/O
    Input address: 2036
    User information available
    Diagnostic interrupt from substitute
    Requested OB: Diagnostic interrupt OB (OB82)
    OB not found, or disabled, or cannot be started in the current operating mode
    External error, Outgoing event
    03:06:00:169 am 06/30/12
   
   
    Event 9 of 100: Event ID 16# 3842
    Module OK
    Module type: Distributed I/O
    Input address: 2043
    User information available
    Diagnostic interrupt from substi

以下是关于《西门子CPU315停机求助》论题的回复(共3篇)

回复人:maliangliu 

 回复时间:2012/7/3 9:48:00

支持(397) | 反对(605)

 

    重启啊

回复人:glenxu 

 回复时间:2014/9/12 12:29:00

支持(407) | 反对(421)

 

    以上信息已经给了你提示,请在OB0中添加OB80、OB86等必要的块,编译下载即可

回复人:15871195606 

 回复时间:2019/12/23 7:59:00

支持(255) | 反对(412)

 

    学习了

如果要回复本栏论题,请首先中国工控网www.chinakong.com

·如果你已经是中国工控网www.chinakong.com成员,请直接登录。

·如果你还不是中国工控网www.chinakong.com成员,请首先注册,注册为免费!

注册名:

密  码:

           注册中国工控网www.chinakong.com
           忘记密码

关闭该窗口

关于我们     免责声明     服务项目     广告联系     友情链接     联系方式     意见反馈     设为首页     加入收藏

 ©2023-2025 中国工控网(www.chinakong.com) 版权所有 豫ICP备17046657号

管理员信箱:chinakong98@163.com  服务热线:13525974529

洛阳博德工控自动化技术有限公司

中国    洛阳